Search found 80 matches

by FireTech
Fri Apr 22, 2011 4:52 pm
Forum: EST3
Topic: SIGA-SD Maintenance Alert
Replies: 8
Views: 8767

Re: SIGA-SD Maintenance Alert

I know you said the Personality Code Changed, But I still want to mention the SD Cover. If that Clear Cover isn't secured properly, It gives you awkward Troubles. I did see in some documentation where you have to restart the SDC card after the cleaning process. I thought this was to get rid of Envir...
by FireTech
Thu Apr 21, 2011 3:06 pm
Forum: EST3
Topic: SIGA-SD Maintenance Alert
Replies: 8
Views: 8767

Re: SIGA-SD Maintenance Alert

In Reviewing the Siga-SD Cleaning Attachment Instructions, It says to take the Slc Loop off (Pwr Down) Take the entire board out and clean everything thoroughly. I only clean like this if needed. (IE- You can visibly see dirt/contaminants in the detector.) Like I said Previously, "When these SD...
by FireTech
Thu Apr 21, 2011 10:48 am
Forum: EST3
Topic: SIGA-SD Maintenance Alert
Replies: 8
Views: 8767

Re: SIGA-SD Maintenance Alert

See Attach Document(s) Re--Siga-SD Cleaning / Testing Methods...
by FireTech
Thu Apr 21, 2011 2:31 am
Forum: EST3
Topic: how to hide the troubles
Replies: 5
Views: 4914

Re: how to hide the troubles

wtf? hide the trbls? Post a list of Troubles , and we can instruct on how to fix each trouble.
by FireTech
Wed Apr 20, 2011 4:28 pm
Forum: EST3
Topic: Printer - not always printing alarms
Replies: 3
Views: 3229

Re: Printer - not always printing alarms

Is the point you test the same point that the customer says is giving a problem? I would check---- 1-) Est3 Message Routing in SDU program. (I see First Alarm in Message) Prints, Check routing. 2-) Do you have Dip switches set properly on printer for use with est3 and Baud rate? If you want, you can...
by FireTech
Wed Apr 20, 2011 4:22 pm
Forum: EST3
Topic: SIGA-SD Maintenance Alert
Replies: 8
Views: 8767

Re: SIGA-SD Maintenance Alert

When these SD Duct smks go into Mait Alert, I "Douche" the Siga-SD. Meaning, open up the detector and give a couple bursts of air around / inside detector. But that is almost useless. I have found that the customer has to First Replace the filters in the Duct work where the detector is dir...
by FireTech
Wed Apr 20, 2011 4:16 pm
Forum: FireWorks
Topic: FireWorks Error. (Tough One to say the Least)
Replies: 0
Views: 2905

FireWorks Error. (Tough One to say the Least)

I am running Fireworks Version.1.5. with 30 Est3 Nodes. 10k Points. With "PAS" "Positive Alarm Sequence" When Fcc Tests "P-1"'s (IE-Pulls,Flows,etc) They have 15 seconds to hit the "PAS" Button. The "PAS" Button Turns every SPK/Strobe/Relay OFF-LOW. ...
by FireTech
Thu Mar 24, 2011 5:26 pm
Forum: EST3
Topic: SIGA-IB operation problem
Replies: 1
Views: 2705

Re: SIGA-IB operation problem

Isolator Base SIGA-IB, SIGA-IB4 - This base includes a built-in line fault isolator for use on Class A circuits. A detector must be installed for it to operate. The isolator base does not support the SIGA-LED Remote LED. The isolator operates as follows: - a short on the line causes all isolators to...
by FireTech
Sun Dec 12, 2010 10:24 pm
Forum: EST3
Topic: EST3 - System goes into Alarm During Download
Replies: 6
Views: 13592

Re: EST3 - System goes into Alarm During Download

Leo,
Were all the CPU's completely Loaded with "Stand alone DB Alarm option" before you had the unprogrammed device on your SSDC card?

Did you remember to Compile and Convert CPU databases after you made this change? And before you downloaded?
by FireTech
Sat Dec 11, 2010 7:26 am
Forum: EST3
Topic: Communication problem
Replies: 12
Views: 12859

Re: Communication problem

Ahmed,
I am glad info was helpful. If your company ever needs any assistance with Est Stuff, Let me know..... Leo and I would love to visit Egypt or the middle east to offer some help.

jimm